Structural integrity?

Hello. This is a brand new deck system as of 2 months ago. I noticed that not only were 2/3 horizontal supports off center, but also, 2 joist hangars are snapped.

I live in MN and this is the code requirements
https://www.dli.mn.gov/sites/default/files/pdf/res-decks.pdf

I contacted the builder and he said the support posts didn’t move (despite obvious slide marks) or shift. He also said it was nailed on the end where the broken joists are and it was done so to make it straight.

It seems it isn’t or wasn’t square to begin with and should a single 6” x 6” horizontal support been used rather than 3 2” x 6” ’s?

Vertical and horizontal cracks on wood too?

Thanks for feedback.

Thanks for the feedback all:

Seeing as work needs to be done, several questions:

  1. What is the best way to lift the deck platform to add/adjust horizontal beams?
  2. The builder insists the vertical supports didn’t move, what else would explain the misalignment?
  3. Best way to secure end/mid posts attachment is Simpson Ties?
  4. Do the 3 horizontal beams need to be bound together?
  5. Anything else besides the obvious?

Appreciated much!

512 Upvotes

596 comments sorted by

100

u/mr_j_boogie 3d ago edited 3d ago

You can use a couple 2x6 boards to lift the deck assembly up an eighth inch to scoot your posts directly under the beams. Then install appropriate hardware.

Editing to add: after zooming in, I see the problem. He used inadequate hardware to attach posts to the beam. Those are for securing the joists to a beam underneath. You'll need to slide something like a Simpson cc66 in there and fasten per spec

79

u/Principletrade 3d ago

I'd tell the yahoo that just built the deck to do that stuff.

53

u/xxK31xx 3d ago

I hear you, but I wouldn't let him back on the job. Can't properly nail/size hangers or acknowledge the post to beam connection is wrong means he'll find another way to cheap out.

6

u/Frogalone Structural Engineer 3d ago

I was going to say that. Laugh.

3

u/thegingerbeardman89 2d ago

Nah hire a competent builder, have them fix it. Have them write up exactly how the first goober messed up, document, and sue the goober for the costs.

→ More replies (1)

3

u/MalarkeyPanda 3d ago

This is how i would do it. That weight disparity is going to fuck that beam in a couple years.

4

u/bumpgrind 3d ago

Needs a professional assessment stat. Joists are sliding across the top of the beam, missing knee bracing on tall posts, missing joist blocking over the beam, might even be experiencing ledger board failure which would be disastrous and potentially deadly if anyone is on it (and definitely below it).

2

u/NewHampshireWoodsman 3d ago

Agree this is an east fix but I would not let anyone on that deck till it's fixed or temp braced safely.

2

u/thebiologistisn 2d ago

I didn't even see the snapped hurricane ties until you mentioned them. There have been some forces at play here that I didn't expect.

2

u/jasno- 3d ago

How can you lift it with some 2x6 boards?  I can't visualize how that's possible 

15

u/MrStickDick professional builder 3d ago

With a jack

6

u/Brilliant-Resist580 3d ago

This is the way bottle jack ftw

3

u/AAonthebutton 3d ago

Hell I keep a 3 ton jack in the truck anyways.

→ More replies (1)

8

u/mr_j_boogie 3d ago

The 2x6s need to be slightly longer than your posts or you can put a board on the ground to give you an extra 1.5". You just stand them up underneath the beam. Probably need to sledge a bit.

A 4x4 or 6x6 would make it easier.

→ More replies (1)

3

u/Frederf220 3d ago

Easiest way is put a "slide board" down and cut a post board slightly too long and hammer it in position under. But you might want a standoff so you have room to get the metal in

2

u/hotinhawaii 3d ago

If you set your 2x6 post on about a two foot long piece of scrap on the ground-the top up next to the post and the bottom about a foot away. Then you whack the bottom of the 2x6 toward vertical, it will lift the deck as it moves to vertical.

→ More replies (1)

2

u/norphn83 3d ago

But the 2x6 a little longer than distance between ground and bottom of beam/deck joists, place 2x6 diagonally putting pressure on top or bottom to wedge into place. Then take another 2x6 and use it to ram the other one in direction of making it plumb. It’ll work. I was in a commercial job that was king of a shit show. They had not installed bearing blocks to carry weight down structure and were already on level three. That’s when my co worker and myself noticed a wall on n first floor with plumbing and electrical already installed but the studs were all bowed way out almost to the point of breaking. Guys must have been walking by it for weeks. So me being an apprentice and not k owing what to do I got my buddy and followed his direction. Got an LVL, but it to the height we needed. Jammed it in and used another long LVL and slid it hard on the floor into the other. Gradually we jacked that 3 story old folks home up several inches allowing the studs to relax. Installed the bearing blocks where needed and went back to what we were working on before. I learned most my old carpenter hacks from my guy Butch.

→ More replies (3)

89

u/5riversofnofear 3d ago

I think this is just a disaster waiting to happen. If the hurricane ties sheared off like that, most likely something bad is happening. Look at Photo 4 please.
Best of luck op.

36

u/sleepy2023 3d ago

Hurricane ties are meant to resist upward force, not the lateral forces of a deck this size. Completely the wrong hardware.

FWIW, the beam being 2x6 vs 6x6 isn’t the issue, the inappropriate connection to the posts is.

2

u/jar_of_lies 2d ago

How did the tie break is the real question. They don't just shear off easily for no reason. Something hit the post or the whole deck shifted? 🤔

7

u/sleepy2023 2d ago

They look like Simpson h2.5a ties. The lateral load capacity perpendicular to the wall is 110 pounds (vs uplift of 700). A normal sized adult jumping on the deck could generate that much force. Get 4 people dancing and you’re there too. People jumping up during a game. Not hard to generate that much force. No strike required.

→ More replies (4)

9

u/AskMeAgainAfterCoffe 3d ago

Omg! I didn’t zoom in and see that! Stay off the deck!

5

u/Thump247 3d ago

Oh shit!!! I didn't zoom in. Yeah, they got a problem.

2

u/Gloomy_Gene3010 3d ago

seems like someone hit the posts with a vehicle or something

→ More replies (1)
→ More replies (2)

39

u/MinorComprehension 3d ago

I think you need to have this looked at. Shifted beam, snapped hangers, something is not right.

8

u/Yusuf20904 3d ago

Right—did the deck shift away from the house, or did the posts shift because they weren't plumb? Or both?

4

u/MinorComprehension 3d ago edited 3d ago

For sure. As long as the joists are still well attached to the ledger and the ledger well attached to the house, I would expect the beams moved.

Then again, it could be the framing was forced into square and popped out. Interestingly the diagonal brace connects closest to the post that is still where it should be. OP should do the quick 3-4-5 check for squareness on the external corners.

3

u/Akanan 3d ago

Imo, They didn’t place the post correctly and were lazy to fix it. Maybe Beam square to the house but posts aren’t

2

u/floridagar 2d ago edited 2d ago

I think I'm seeing that the post/beam connection was cut, maybe with a sawzall. Those connectors, even though they're not appropriate, don't just snap off. If there was a force applied that was enough to break them there's no way the beam would still be on the posts. They and their supporting initial nails were cut.

You can see places where the posts were piss nailed through to the beam, they were probably decently connected when the beam was first set. I always make my decks wear their simpsons but framing nails are strong as fuck on their own, more than enough to keep a beam on a post.

The posts came before the beam, then the joists then the deck. The beam was seated neatly on top of the posts when it was set obviously and there's nails to indicate this. The ledger didn't violently rip itself away from the house on just the one side.

edit: the beam span isn't great but it isn't related. There's a critical fuckup here somewhere, the inadequacies are only a distraction.

36

u/Go__Wild 3d ago

Simpson Strong Tie AC

14

u/M_E90 3d ago

2

u/Go__Wild 3d ago

Anything but a hurricane tie lol

3

u/M_E90 3d ago

seriously, lol I wonder what the inspector is going to say.....

3

u/Go__Wild 3d ago

He'll probably take one look, sigh, and walk back to his truck.

→ More replies (6)

130

u/WoodWizards 3d ago

The first thought that comes to mind is that those posts should be plated to the joist.

128

u/Disgrace_To_Humanity 3d ago

Beam

31

u/MesaGeek 3d ago

Thank you for your service.

23

u/soedesh1 3d ago

The first thought I had was about the Sword of Damocles.

5

u/brianbradencody 3d ago

No sir, that’s a replica 😏

→ More replies (1)

2

u/prush1977 3d ago

2 out of 3 stars...

→ More replies (1)

14

u/damagedgoodslol 3d ago

Not to code and not built correctly

2

u/kangarang007 2d ago

Jugothat right 👍

49

u/zitrored 3d ago

My first question is did he pull permits for it? People unfortunately think the government has no place in their lives. This is a good example of where they help you.

9

u/TapDismal4715 3d ago

Not ever place requires permits. Where I live if you're outside city limits you can do whatever the hell you want on your property.

6

u/666MCID666 3d ago

As a production manager, I can assure you this likely is not the case, you just haven't been caught and fined yet.

In the US (speaking from NY, specifically), building permits are needed for a LOT of projects you wouldn't necessarily assume need them. On top of that, those rules change per municipality.

For example: the Town of NYC, the Village of NYC, the City of NYC are allllllllllll different rules, that are then exacerbated ten fold when an HOA is involved.

And I'm not talking common sense stuff, I'm talking like, replacing windows, doors, siding, etc. sometimes it needs a permit, sometimes it doesn't.

I will say though, it's rare, but there are towns scattered here that are small enough that the county is then responsible for, but still needed.

2

u/kvnr10 3d ago

NYC is certainly not the most representative sample of this country. In many places people don't get permits for a lot of things and if someone finds it it was there when you moved in. Right or wrong, in the real world a rule without enforcement is a suggestion.

→ More replies (1)
→ More replies (6)
→ More replies (6)
→ More replies (7)

12

u/HopefulAnt2476 3d ago

A quality contractor would show up and correct it at no charge. Musta been a white line guarantee.

Knee braces are missing also.

21

u/Wilbie9000 3d ago

The only thing with less integrity than that structure is your contractor.

→ More replies (1)

8

u/GreenCarpenter3 3d ago

Another real concern is that there isn’t a steel bracket holding the beam to the post. You need something like this or a similar product

6

u/Lame_Coder_42 3d ago

He has a triple on a 6x6 so he'd need two offset brackets to account for the beam being narrowed than the post. 

2

u/GreenCarpenter3 3d ago

Alternatively, OP could use PT plywood to add width to the beam. I’m pretty sure that is what Simpson recommends.

→ More replies (1)

8

u/Alph1 3d ago edited 3d ago

I've never seen ties broken like that. Fortunately, Simpson sells a bracket that would be able to secure the beam onto the posts. But I would want to know why the ties (which never should have been used there) broke like that.

I'm also not seeing what's holding together the triple beam. It needs lags or even a carriage bolt.

3

u/skipnstones 3d ago

Yea those clips are for resisting uplift not shear, I’m not a structural engineer, but I think those were inappropriately used in this situation…

2

u/kevingrays 3d ago

100% they should have used a post to beam connector. Those ties he used are for vertical hold down, usually rafters or joists. The beam and has definitely shifted on the one side. If this contractor is licensed, you can report them if you're not getting the deck built to code.

→ More replies (1)

2

u/Eastern-Course-7975 3d ago

From the look of it they’re being held together by hopes and prayers.

→ More replies (1)

16

u/Ryukyo 3d ago

I can't believe all these people saying it's probably fine. At first I didn't know what was going on, then I realized those beams have no positive connection to the posts anymore. The straps broke. That is completely unsafe. Do what you can to safely stabilize that. Gravity-wise it might be "fine" but we don't live in a static environment. Lateral forces are what caused those metal brackets to shear and fail. And it's going to keep happening because there is no positive connection I can see. It doesn't just look like the posts are off center, it looks like the beam and joist framing moved enough to break the improper strap that was there, and now is free to keep moving around. That needs to be addressed.

2

u/MixerMan67 2d ago

I don’t think the beam moved because the hurricane ties on top are still intact. It almost looks like someone broke or cut the bottom ties to plumb the posts. It’s hard to tell from pictures, though. Other than missing the proper connectors, this deck looks pretty sturdy.

→ More replies (1)
→ More replies (2)

15

u/[deleted] 3d ago

[deleted]

3

u/vertsav 3d ago

Many areas (such as mine and the 4 other counties around I work in) have no inspections on decks, so it’s entirely possible OP area is the same situation

→ More replies (1)

3

u/MickeyHoldem 3d ago

If you zoom in to the 4th photo... you can see the beam is larger than the joists... if the joists are 2x8 then the beam is a triple 2x10... assuming a 16" spacing for the joists makes the beam about 16 feet... so 8' spacing between posts... perfectly adequate.

For sure this deck has issues... it need better connections between posts and beam... get the appropriate simpson connector... you can see a broken strap which was obviously inadequate.

There needs to better lateral bracing considering how tall the posts are.... how much and what type should be designed by an engineer...

But seriously... those aren't 2x6s... and with proper bracing and new post-beam connectors... this isnt the problem everyone seems to think.

→ More replies (25)

8

u/20PoundHammer 3d ago

well, the beam is not tied to the post any more (ties are broken). I quad up that beam and then use a plate or tied to fasten it to the post. Not sure if all the posts warped - the deck moved or it was just built like this. If you ever have 30+mph sustained winds - this deck is really sub-built. I would quadruple up the blocking and put is sway braces (diagonals) post to beam as well.

I am very curious how the header is attached. This looks pretty sketch and very likely would not have passed an inspection in my area, esp now since all the ties are broken.

the cracks on the posts are called checking - doesnt matter a lick for post integrity.

9

u/ThereInAFortnight 3d ago

My main concern would be this: What force caused the misalignment between posts and beam, and is it still acting.

5

u/Bright_Crazy1015 3d ago

If I had to guess, all this lumber was likely saturated when it was stood up, and since then has dried out significantly. Being long posts with no support between either end, the brackets need to be more substantial than a small hurricane strap that was never meant to deal with anything but uplift. As they dried out, they put some tension into the straps and the straps resisted until they broke, thankfully, or it would likely be worse. Significant twisting, etc.

Powdercoated steel decorative timber brackets are what I would use to fix this. I'll eat the 1/4"- 5/16" of material gained over that span. I'm not pulling the posts out to cut off a quarter inch with a ~10' span

9

u/Departure-Sea 2d ago

Got the integrity of a politician.

15

u/throw-away-doh 3d ago edited 3d ago

The triple ply beam is fine and normal.

The problem is that the builder did not correctly connect the top of the post to the beam. Your builder used hurricane ties, which are for joists. That should have failed an inspection. He needs to use metal post caps. You want the BCS2-3/6Z

https://www.strongtie.com/onepiecepostcaps_postcaps/bcs_cap/p/bcs

Have the builder come back and install the post caps.

2

u/Possible_Mammoth_879 3d ago

That's such a simple fix, makes you wonder why he didn't use those?

2

u/huzzah3x 3d ago

Easy to put on while building. Harder to retrofit with the weight of a fully built deck on top of it.

Something else reliable will need to be used, perhaps heavy duty plates of some variety, or something custom formed so that all the stress force isn't wanting to just push the nails or screws out. Certainly not just a puny joist hurricane tie. That should never have passed inspection. I'm guessing no inspection here.

4

u/throw-away-doh 3d ago

Yeah you would need to jack it up 3 inches to put these on as a retro fit.

Another option is these.

https://www.strongtie.com/twopiecepostcaps_postcaps/lpc_cap/p/lpcz

You put a pair of them on each post and can slide them into a retro fit situation.

2

u/Lame_Coder_42 3d ago

If you look closely at the triple there's one nail about every 2 foot, and no staggering. Also triple 2x6 can only span about 7 foot max. Would not call that beam "fine and normal". Not built to code, probably not cause an issue if they go back and staggered fasteners and brackets. Unless they throw a deck party and have a heavy live load it should survive.

The most likely "fix" that will happen is recentering the beam and adding the correct beam/post connectors. 

It's weird because they actually used deck to house tension brackets. Which is a bracket most guys don't know exist or use, lol. But didn't double up the rim joist? Idk, maybe couple guys tag teamed the build...

2

u/TelevisionTimely3918 3d ago

Those don’t look like 2x6s. Look at the last picture.

→ More replies (1)
→ More replies (1)

6

u/Euphoric_Two_4469 3d ago

The contractor used hurricane brackets to secure the posts? I see the snap. Then they toed the posts? You maybe able to fix this to all posts on both sides.

6

u/Euphoric_Two_4469 3d ago

You can do this too, which would probably be better. You’ll have to cut 1/2 p.t. plywood to fill the gap.

5

u/Burghpuppies412 3d ago

That looks like a better fix to me. And maybe easier to monitor future movement, if any.

→ More replies (3)

7

u/Significant_Onion_25 2d ago

Cause 2 outta 3 ain't bad...

6

u/Goldtacto 3d ago

Beams need a beam to post bracket. There are a couple options for that.

You're supposed to have blocking over the beam for code with that cantilever.

Vertical cracks are ok here. It's called checking and it's normal.

10

u/Lame_Coder_42 3d ago

A triple 2x6 as a deck beam shouldn't be spanning over about 7 foot and needs beam/post connectors to help prevent exactly what happened. Unless your joists are 12" on center your beam is not to code. Hurricane hangers do zero for lateral loads and this is miss application. You should really check if the joists and ledger are installed properly. It appears the deck pulled away from the house and shifted on the beam. Get an inspection asap and be ready to pursue legal steps as the contractor doesn't appear to have had a clue about deck construction or building codes.

→ More replies (2)

5

u/Material-Truth5457 3d ago

It looks like two posts shifted and snaped their ties and both are off by one ply. The third post totally support all three plys . The only thing that moved seems to be the posts and after the ties were in place.

→ More replies (4)

3

u/Ill-Studio-1742 3d ago

Add some post to beam connections.

2

u/whiskeyandweiners 3d ago

The beam needs to be sitting completely on the post. Also there should be mounting hardware at the intersection between the post and the beam. If your builder is not going to fix it. Hire someone else to do it, and send the original builder the invoice.

5

u/xrayguy1981 3d ago

Go ahead and get ready to lawyer up or take him to small claims court. Based on his response he isn’t going to be very willing to do anything without a little encouragement.

4

u/El_Galant 3d ago

Poor. There's no connection between the beam and the posts. That deck will slide right off with a little time / rain / snow /weight / wind - if windy the uplift will take care of the detachment quickly.

4

u/dudeitsadell 3d ago

hurricane tie literally snapped lol

5

u/alpha_cool_bruh 3d ago

lmao at the builder throwing any ol' Simpsons product up there.

I don't understand how a deck builder could not just get a proper bracket for this connection.

2

u/NineClaws 3d ago

$30 max?

4

u/Affectionate-Aide422 3d ago

That’s gonna slide off the posts sooner or later. Sooner if you are in earthquake country.

2

u/workinhardplayharder 3d ago

Looks like sooner regardless of earthquake country. If it's a new build and it's already snapped the brackets that they thought would hold it and moved that far

4

u/Gambyt_7 2d ago

“Of course he was the lowest bidder. We didn’t have to pay for any permit. Why do you ask?”

7

u/justme0000001 3d ago

That doesn't even have moral integrity

→ More replies (1)

6

u/Quirky-Entry-590 3d ago

I’d call this one a politician if we are looking for integrity.

3

u/Wiedzmaki 3d ago edited 3d ago

Lol that's just sitting on there with no grooves or brackets?

3

u/noway7454 3d ago

You need the proper hardware between the posts and beam, something like this

→ More replies (2)

3

u/Fair_Discipline_1875 3d ago

Looks like an unpermitted un-inspected deck.

Time to get the county involved before it’s too late.

→ More replies (2)

3

u/Firm_Analysis5131 3d ago

It can either be fixed now while it’s relatively easy or fixed later after this problem gets worse and part or all of it falls down.

3

u/lelio98 3d ago

I would take immediate corrective action. Posts look like 6x6? I’d sandwich them with a full length 2x8 that cradles the beam with multiple through lags.

That or some beefier Simpson ties with lags, or both?

Not an engineer, but that beam is just sitting there waiting to move and fail.

→ More replies (2)

3

u/1Fistfullofdollars 3d ago

They could have very easily moved that over to fit better. There is lots of room on the other post . Planning would have helped .

3

u/woodchuckernj 3d ago

so the fact that it's not tied down is a red flag. Why they didn't put the tripple beam on top of the post is bizarre. It wouldn't cost them anything. There is a problem here, it's the lack of a tie in.

You need to get the builder to fix it! If they won't take more pics and go to court. Was it built with a building permit?

2

u/Frogalone Structural Engineer 3d ago

I agree with what Chuck said. You need to take some smoking gun pictures. Go around and look for things out of plumb, not square, unexpected translation (horizontal movement), missing hardware, obvious signs of distress, etc. Best of luck. It really gets me mad the way things work. A contractor can screw things up and it takes an act of God to hold them accountable. I suppose I'm deranged, but it would be nice to hold part of the payment until after inspection. Your a daisy if you do.

2

u/Routine_Election4188 2d ago

The contractor is obviously a hack. Is it possible to have a competent contractor make repairs and sue the original contractor for cost?

→ More replies (1)

3

u/Frogalone Structural Engineer 3d ago

I'm having trouble understanding how the deck main beam can slide on the post rather than just causing them to lean out-of-plumb. Also:

  • There should be proper post-to-beam connection so the beam doesn't fall off.
  • There should be blocking between joists at the beam line.
If you can cite a couple of code violations it might help.

→ More replies (4)

3

u/Historical_Wheel1090 3d ago

That is NOT up to code in my area. Beams aren't allowed to stand on the top of a post like that. They have to be installed in a way that they won't roll over.

Did you pull a permit to get this built?

→ More replies (1)

3

u/HOLLYW00D78 5h ago

Does this make anyone else curious what the the footings and ledger look like?

4

u/mddale1 3d ago

I think builders should not drink on the job.

2

u/Icy-Medicine-495 3d ago

Using multiple 2x6 instead of 1 giant beam is normal but those hangers snapped and you need something to resecure it. Although if the beam is actually only 6 inch boards that is probably undersized.

3

u/kstorm88 3d ago

Yeah, those look like 2x8's, 2x6's wouldn't cut it where I live with that cantilever

2

u/Fearless_Adventures 3d ago

Those are the smallest $2 hardware straps that lowes carries. I used them on some rafters on a shed. Wouldn't even consider them for this

2

u/randomhero0679 3d ago

Did they use OSB plywood for the trim pieces? Obviously if they did, not structural but that would be a clear indication of the type of work they do 🤦🏻‍♂️

2

u/Berd_Turglar 3d ago

This design is no bueno, i think there should be shear bracing of somekind on that beam assembly, and those posts should definitely be securely attached to the beam. Even then whats the prevent this whole thing from just folding flat if theres high winds or an earthquake or something? Seems like that one diagonal brace 2x4 on the jojsts is doing some very important work there but gat damn i cant imagine an engineer would be into any of this. If im wrong would love somekne to school me on that

2

u/Beamin1988 3d ago

WOAH WE’RE HALFWAY THERE, WOAH, LIVIN’ ON A PRAYER!

2

u/zonedkay 3d ago

Ah the hopes and dreams method

2

u/Bolt_release 3d ago

Is the “Structural Integrity” in the room with us now?

2

u/Livinginmygirlsworld 3d ago

I'm curious what the connection (if there is one) at the bottom of the posts is.

Probably didn't include this either:

The lateral load connection required by Section R502.2.2 shall be permitted to be in accordance with Figure R502.2.2.3. Hold-down tension devices shall be provided in not less than two locations per deck and each device shall have an allowable stress design capacity of not less than 1500lb.

2

u/Rare_Fig3081 3d ago

I love the one toenailed attachment

2

u/Fickle-Date1922 3d ago

Those look like 2 x 8 or 10’s, that beam should be screwed together and fully bear on post. I don’t get your contractor’s explanation of how that post shifted. I believe Simpson makes an appropriate connector for that application, hurricane ties are not it! Curious what connection at house is? Did that shift? Are we going down?

2

u/Positive-Sound-4972 3d ago

I hope the big bad wolf doesn't come

2

u/Neither-Ad-6770 3d ago

This is called the faith in friction only method. Commonly used in those who dont beleive in vibration or wind.

2

u/z13critter 3d ago

Those hurricane ties are not the proper tie for post to beam connection… these should have a bcs galvanized post cap connecting the posts to the beam…

2

u/Cthulhu_HighLord 3d ago

Basically your deck is free floating, a strong enough wind and your deck is going to rip the wall out, then you'll have internal structural damage at the base mounts of the wall as the weight pulls down causing it to split. Secure with the correct bracketing

2

u/Unable-Boysenberry24 3d ago

The last photo is interesting. Look at the hurricane ties sheared off at the beam-post connection.

2

u/Kenkley3 3d ago

Minor point: If that fascia is OSB, and it appears to be, leaving the backside unfinished is poor practice, particularly on an elevated deck exposed to moisture. OSB is especially vulnerable to moisture at its edges, where water can penetrate, cause swelling, and eventually lead to deterioration. Even exterior-rated OSB is not intended to remain exposed indefinitely.

2

u/Sea-Veterinarian1905 3d ago edited 3d ago

Proper metal connector should’ve been used. Looks like a hurricane tie was used

2

u/crispt89 3d ago

Yea this is not good, they definitely poured footings out of square and moved framing to compensate for it.

2

u/Iambetterthanuhaha 3d ago

Need to get up there with a sledgehammer and some Simpson strong ties. Pound that one 2x6 onto the post and screw braces on. Should buy you some time till you can add additional posts/bracing.

2

u/CaterpillarAnxious97 2d ago

Looks like you drove something into those (2) posts by accident.

2

u/Dendady2112 1d ago

I'll say it again. Just move the beam.

2

u/DefiantNewspaper8725 22h ago

I didn't read every comment so I might be repeating some previously said things... But is the beam even laminated? It doesn't even look to me based on the gaps from the underneath photos like the beam is properly fastened to each other and are they even big enough for the span between posts?

As said previously, they needed to use a proper post to beam connector which they didn't..

Is the beam 2x8? Or 2x10? Doesn't look big enough to be 2x12. Not sure what your joist span is but this would be easy for you to check if they even used the right size lumber for your beam span based on spacing between posts and your joist span.

3

u/TheXenon8 3d ago

Sheared off hurricane ties within 2 months is a horrible sign. That thing is falling and it’ll be on the ground soon. I’d take this to court if he doesn’t agree to fix or pay for a different contractor to fix as I would not let him touch anything else

2

u/frealdough 3d ago

I would put another 2x on the beam. If you cant squeeze it up there, put a relief cut at the posts. The extra piece will be proud on one end and bear completely on the other. Clamp it tight and use structural screws to keep it together. Then create a gusset out of wood to tie the post and beam together.

Keep it pimp tight gnome sayin

2

u/Catcherinhereye 3d ago

Aint nothing here to be proud of. I’ll see myself out….

→ More replies (1)

3

u/Revolutionary-Gap-28 3d ago

You're good structurally. But it's really easy to adjust the posts, so I'm not sure why they are so off center. The mounting plate to the concrete footer moves.

11

u/xxK31xx 3d ago

It's not good structurally when a third of the beam is no longer bearing and hangers have snapped. Aside from contractor halfway doing the job, this could also be frost heave.

9

u/ThereInAFortnight 3d ago

Define "really easy"

2

u/Significant-Ear-3262 3d ago

Easier than building a Stargate in your basement out of 100 pounds of titanium, 200 feet of fiber optic cable, seven 100,000 watt capacitors, and a toaster.

→ More replies (4)
→ More replies (1)

4

u/20PoundHammer 3d ago

its not really easy as it moved over 1.5" judging from the snapped "tie" shown in the pic. You also have zero clue on what footer connection (if any) was used as nothing is shown. Even if it is standard one, you only have <1" of wiggle.

3

u/Salt-Replacement596 3d ago

It's not good ... especially not structurally.

4

u/Shot_Boot_7279 3d ago

Your assuming there are mounting plates. Many counties allow treated deck posts to be set in concrete.

3

u/Sufficient_Cow_6152 DIYer 3d ago

Also, if mounting plates were used, maybe they are already offset as far as they can go.

→ More replies (3)

1

u/fuxuandyourhorse 3h ago

Looks good from my house

1

u/UpbeatAssociation649 2h ago

Its been said but a 4x4 and a bottle jack is easier than a 2x6. Use the correct hardware set it back down

1

u/dap00man 3d ago

It looks like nothing is actually tying it down to the post

1

u/xxK31xx 3d ago

You are right to be concerned. I would keep people off the deck until it's fixed. I would not bring back your builder, bc it seems like some obvious corners were cut.

Footer depth needs to be checked if you are in area that drops below 32 in the winter. Are you in an area that permits are required? Call the city/county to make sure.

1

u/confident_cabbage 3d ago

Even if sound I would be pissed of I spent money on it because it looks stupid.

1

u/hitchhikereditor 3d ago

It’s not attached so there is that. Attach it and it won’t wiggle so much thus improving structural stability

1

u/YamComprehensive7186 3d ago

Missed it by this much!

1

u/dunncrew 3d ago

"2 out of 3 ain't baaad" - Meatloaf

1

u/jradz12 3d ago

2x10 or 12 w.e is hanging off is literally doing nothing. Seems concerning

1

u/joebyrd3rd 3d ago

I think that you have more issues than just the bean not setting on the supports. And why did that strap fail. That's all big time shit. I would not let that contractor back on my property.

If you look at the photo from under the deck looking out, there is a joist which has been "sistered" to. Why? The actual joist seems cut short and doesn't reach the rim joist. It appears that a small block was put in to fill the gap. The sistered piece was put in to actual support that outside rim joist.

I'm confident that there's more, much more. Find a inspector, have it inspected, and go from there.

2

u/Phatmac-pie 3d ago

Id go with this one OP.

1

u/FarFromHome75 3d ago

What's less than Zero

1

u/uslashuname 3d ago

> 2 joist hangars are snapped

The things against your house snapped? Or do you mean the straps between the posts and beam, shown as snapped in the photos?

Obviously you got comments on the straps already, but if you also have joist hangars snapping where they’re attaching the deck to the house that’s a major concern

1

u/country_dinosaur97 3d ago

Thats cause by the looks of what i can see they used hurricane ties not post caps or beam straps what they used is meant to handle upward forces not so much side to side. Look up this " LPC6Z hanger" thats closer to what you should have there

1

u/SM-68 3d ago

Put a 2x8 on the opposite side of the posts. Will look even and more bearing on post.

1

u/bigdaddy9901xy 3d ago

Could they not have at least centered the post? Would have taken like 2 minutes

1

u/Much-Cardiologist300 3d ago

Time for a hot tub in the deck

1

u/Impressive-Sky-7006 3d ago

The footings are probably in the wrong place.

1

u/PsychologicalTea1888 3d ago

That’s a lawsuit waiting to happen.

1

u/Imaginary_Agency_424 3d ago

Ibwould have him move post to center under the beam and install some sort of mechanical fastener. 3- 2x6 is fine but i wonder whuy he didnt use a bigger piece of limber at least 2x10.

1

u/ToughDesigner7072 3d ago

Oh boy…. Don’t use it at all.

I’d be seriously concerned about it falling and collapsing, killing someone.

You’ve got nothing holding the posts to the platform except gravity.

Those hurricane ties are completely misapplied.

It’s like half the deck was built by someone competent and the other half was built by someone who looked at what the other guy did and decided, I’m going to do the opposite.

Why is the other side of the joists not supporters by hangers?

And you don’t have a beam - just some boards sandwiched together. Are they all like just glued?

I’m surprised you made it 2 months like this.

Seriously - call a professional right now.

→ More replies (3)

1

u/GramophoneDrums 3d ago

Were they building off of plans or just freehanding it?

1

u/UrNoTsHu 3d ago

If you squint its mint!!!!

1

u/brianbradencody 3d ago

You’re just noticing 2 mos later?

3

u/ToughDesigner7072 3d ago

Sadly, wasn’t educated enough to catch the wrong ties being used, or any other issues. And yes who goes looks at the underside of their deck each day? Probably didn’t realize when they snapped or beam and post connection started to shift until a couple of weeks ago. Hoping someone here would waive it off while they continue to enjoy their coffees having paid someone a sizeable chunk and assuming they got a lifetime worth of deck built up. Poor folks.

Screw the contractor who did this. And people argue for more pay or freedom for contractors but they keep screwing their customers like this. I don’t think they were malicious. Just lazy and didn’t bother to study how to build a deck that lasts or why not to use cheap hurricane ties in this application.

2

u/Significant_Raise760 3d ago

I'm super confused as to how it got this way. My theory is that they built the deck, then noticed the posts were not straight up and down, and sledge hammered them over 1.5" to make them vertical. That broke the ties, and they just nailed it back. Overall, a crappy way to fix a mistake. I would definitely have a heart to heart with the builder, about how he's going to pay for a real contractor to fix this shit show.

→ More replies (1)

1

u/imastocky1 3d ago

Slight

1

u/Bneff14 3d ago

A lot of omg this is going to kill someone here. Is this how a finished deck I built would look? No. But its far from life threatening. They likely set the post saddles centered on the concrete piers(assumption) which is why one is centered for the beam and the other 2 are 1 1/2" off center. There is still plenty of the weight transfer happening as long as the beam is nailed properly.

Also, there are millions of decks out there built without modern steel connection fasteners. 3"nails properly set from the beam to the post will hold fine. That being said a properly installed connection strap/plate is cheap insurance. And required in seismic areas. But the posts are not going to "easily slide out" from the thousands of pounds of compression.

If a contractor was paid for this work, I would certainly be withholding payment until a few of these issues are resolved. Otherwise if it has been paid for, and there aren't explicit plans and a contract you can cite its not worth your trouble. Threaten to leave them a bad online review if possible? Otherwise invest the money in having someone else come in to do the minor modifications to will just make it a bit stronger/safer. But it is certainly not in danger of falling over.

→ More replies (5)

1

u/Stunning-Material888 3d ago

Question is was it fine when finished or like this? Since it’s snapped I would the post or concrete below has moved. And moved enough to obviously cause pressure. I would get others involved if the contractor is not caring.

1

u/gligster71 3d ago

I am a total hack amateur woodwork enthusiast, but I cannot for the life of me see how anyone can NOT line these things up. It would drive me crazy. I would have to tear the post out and re-do it if that was the only way to fix it.

1

u/pogiguy2020 3d ago

Id have the city building inspector come out and give them the number to this contractor. let them tell the contractor what NEEDS to be done.

1

u/Possible_Mammoth_879 3d ago

Wouldn't it been smart to fix two steel plates on each side overlapping by 12 Inches? You could fix them in with deep screws and lock it together tightly.

Surely that's enough and is doable now too?

1

u/ilovebourbon13 3d ago

Hey boss! What are these leftover metal things for?

1

u/timjbd 3d ago

Where’s the hot tub sitting?

But seriously, 3 glued/screwed 2x6 are better than a single 6x6. The builder should absolutely remedy but not so sure, after looking at his work, I’d want him applying any remedy.

1

u/Agile_Season_6118 3d ago

This little bitty hurricane straps are so small I didn't even notice them at first! Go big or go home.

1

u/kenibus 3d ago

That wood moved for sure. Which isnt cool. I mean you have snapped hardware as evidence. Are the posts plumb?

Dude needs to fix it!

1

u/alexjnorwood 3d ago

This makes me very nervous. Just need a better connection between that beam and the posts

1

u/Bright_Crazy1015 3d ago

Be careful lifting this onto a temporary support to fix it. There's obviously tension and I'm not so sure the post wouldnt vacate it's..er... post.. once all the weight is lifted from it. I'd strap a chunk of 2x6 to the post so it can't fall backwards and shift all the weight suddenly onto a temporary support. If you can lift it on scaffold that would be a safer bet.

If 5he footers are fine and the post connection is the only problem, this is a half a day fix to put decorative timber brackets on with lags. Lift the deck, slide them in, lag it, done and on to the next.

1

u/Level-Status-5629 3d ago

Holy gravity fear! Lol

1

u/turkeylurkey324 3d ago

What does the footing look like? Post sunk in ground? Helical screw footing? If there is a poured concrete footing in a tube that is 16-24” diameter, you could support the existing beam, move and connect the posts to new spot on footer so they are all fully under beam, and put correct post to beam connector on. The beam really needs to fully bear on each post.

The rest of it doesn’t look bad. Wood cracks/checks. If it was too damaged at install, it shouldn’t have been used.

I didn’t look it up, but refer to lumber spanning tables for correct beam size. I can’t tell if that beam is 2x6 tripled or 2x8’s. It looks like 2x8’s.

1

u/Open_Unit_4486 3d ago

Just put really thick mattress under , it should do 🤷‍♂️

1

u/CO8127 3d ago

Close enough😉

1

u/LukissxD 3d ago

On the case of structural integrity... We have no structural integrity

1

u/CryptoNurse-EcC- 3d ago

2/3’s of the way there

1

u/Former_Anybody3541 3d ago

No way building inspector passes that. Wow

1

u/Decent_Ad5361 3d ago

Supposed to use a post cap in that situation.

1

u/Ippus_21 3d ago

I'd about bet those posts weren't fully dried and they warped after installation. The alternative is that the footings somehow shifted.

The fact the ties are missing and 2 of the posts only support 2/3 of the beam definitely seems like a problem to me.

And it raises the question of whether they're still not done shifting.

It sounds like the builder just doesn't want to be responsible for fixing it. And given that, I wouldn't trust him to fix it right.

1

u/Gregan32 3d ago

Throw a fourth 2x on there...

1

u/Masta_T1 3d ago

Death trap waiting to happen.

1

u/Ginga_Ninja006 3d ago

It’s missing lots of safety features and the fact that it’s twisting off the beams is evidence of that.

1

u/40two50 3d ago

Need to get yer money back. Then hire a deck retrofit guy to make things better. Not sure this will ever be safe tho, not without a laminated beam on top of posts properly bolted down with engineers heavy gauge hardware. Wood rot is gonna develop between the 3 2x’s supporting everything… not safe. I give it 1-3 seasons at best… with nobody using it… just as a sculpture to admire from afar. With regular use… u risk death.